Way OT - refrigeration question
I know we have a few refrigeration experts on here, so maybe y'all can point me in the right direction.
I have a Danby Silhouette under-counter beverage cooler that's about a year and a half old. It's lowest setting is 39 degrees, which it used to be able to hit, or at least 40-41. Now, it won't usually get below 47, and after I have a few (not quite ice-cold) beers, it's at about 50.
It's definitely cooling, but not like it was before. Most of the web troubleshooting points to things where it isn't cooling at all, which isn't the case here. (Some have mentioned a new humidity controller but I don't know). I did try to empty stuff out so air would circulate better, but that didn't seem to help.
One thing - when we lose power the setting resets to about 54, and I have to turn it down again, but I can't see how that might be relevant.
My level of handiness is pretty much limited to screwdrivers and pliers (and the occasional drill and miter saw), so hopefully there is a simple solution?
Thanks for any input.
I have a Danby Silhouette under-counter beverage cooler that's about a year and a half old. It's lowest setting is 39 degrees, which it used to be able to hit, or at least 40-41. Now, it won't usually get below 47, and after I have a few (not quite ice-cold) beers, it's at about 50.
It's definitely cooling, but not like it was before. Most of the web troubleshooting points to things where it isn't cooling at all, which isn't the case here. (Some have mentioned a new humidity controller but I don't know). I did try to empty stuff out so air would circulate better, but that didn't seem to help.
One thing - when we lose power the setting resets to about 54, and I have to turn it down again, but I can't see how that might be relevant.
My level of handiness is pretty much limited to screwdrivers and pliers (and the occasional drill and miter saw), so hopefully there is a simple solution?
Thanks for any input.
NOLA
Comments
-
Paging @NPHuskerFL . The resident AC&R eggspert.Louisville; Rolling smoke in the neighbourhood. # 38 for the win. Life is too short for light/lite beer! Seems I'm livin in a transitional period.
-
I had the same thing happen to my cooler, but within days - I took mine back to costco.
-
BYS1981 said:I had the same thing happen to my cooler, but within days - I took mine back to costco.
NOLA -
I will assume it is a compressor/refrigerant type system rather than a thermocouple solid state refrigerator. My question will be, "is the compressor running constantly trying to achieve the set temp?"
If that answer is "yes" then you either have a poor flowing condenser or condenser fan innoperative. Or the worst case a lack of freon flow due to refrigerant leak or flow restriction.
If the compressor cycles off at a temp higher than the set temp it can be thermostat related or the same dreaded freon flow issue but this time over cooling part of the evap and leaving the rest of the evap without any cooling. That can trick the tstat sensing bulb or thermister.
JimLBGE/Weber Kettle/Blackstone 36" Griddle/Turkey Fryer/Induction Burner/Royal Gourmet 24" Griddle/Cuisinart Twin Oaks/Pit Boss Tabletop pellet smoker/Instant Pot
BBQ from the State of Connecticut!
Jim -
Probably the fan
-
CtTOPGUN said:I will assume it is a compressor/refrigerant type system rather than a thermocouple solid state refrigerator. My question will be, "is the compressor running constantly trying to achieve the set temp?"
If that answer is "yes" then you either have a poor flowing condenser or condenser fan innoperative. Or the worst case a lack of freon flow due to refrigerant leak or flow restriction.
If the compressor cycles off at a temp higher than the set temp it can be thermostat related or the same dreaded freon flow issue but this time over cooling part of the evap and leaving the rest of the evap without any cooling. That can trick the tstat sensing bulb or thermister.
Jim
NOLA -
Their website shows a two year warranty. You mentioned it is only 1.5 years old so I would look i to getting it repaired under warranty.Which came first the chicken or the egg? I egged the chicken and then I ate his leg.
-
SmokeyPitt said:Their website shows a two year warranty. You mentioned it is only 1.5 years old so I would look i to getting it repaired under warranty.
They are sending a repair guy out tomorrow. Woot!!
Thanks, y'all!! Cheers!
NOLA -
Hopefully, they take good care of you!
-
It's the flux capacitor. Gotta be the flux capacitor.LBGE 2013 & MM 2014Die Hard HUSKER & BRONCO FANFlying Low & Slow in "Da Burg" FL
-
BYS1981 said:Hopefully, they take good care of you!
The main problem seemed to be that the door was somehow warped and the gasket wasn't sealing.
NOLA
Categories
- All Categories
- 183.2K EggHead Forum
- 15.7K Forum List
- 460 EGGtoberfest
- 1.9K Forum Feedback
- 10.4K Off Topic
- 2.2K EGG Table Forum
- 1 Rules & Disclaimer
- 9K Cookbook
- 12 Valentines Day
- 91 Holiday Recipes
- 223 Appetizers
- 517 Baking
- 2.5K Beef
- 88 Desserts
- 167 Lamb
- 2.4K Pork
- 1.5K Poultry
- 32 Salads and Dressings
- 320 Sauces, Rubs, Marinades
- 544 Seafood
- 175 Sides
- 121 Soups, Stews, Chilis
- 37 Vegetarian
- 102 Vegetables
- 314 Health
- 293 Weight Loss Forum